To calculate the resistance that must be placed in the neutral for a single-phase-to-ground fault such that the fault current does not exceed the rated line current, we can use the following relationship:
1. Rated Line Current (I_line):
[
I_{line} = frac{S_{rated}}{sqrt{3} times V_{LL}} = frac{10 , text{MVA}}{sqrt{3} times 11 , text{kV}} = frac{10 times 10^6}{sqrt{3} times 11 times 10^3} approx 523.6 , text{A}
]
2. Fault Current (I_f) for a single-phase-to-ground fault:
– For a single-phase-to-ground fault in a generator, the fault current is determined primarily by the zero-sequence reactance (X0) since only one phase is involved.
– The relationship for the fault current is:
[
I_f = frac{V_{LL}}{Z_{fault}}
]
where (Z_{fault} = R + jX_0).
Given:
– (X_0 = 10% text{ of } Z_{base}).
– (Z_{base} = frac{V_{LL}^2}{S_{rated}} = frac{(11