To determine the resistance that must be placed in the neutral for a single-phase to ground fault such that the zero sequence fault current does not exceed the rated line current of the alternator, we can follow these steps:
1. Calculate the rated line current (I_line) of the alternator using the formula:
[
I_{line} = frac{S}{sqrt{3} times V_{line}}
]
where ( S ) is the apparent power in MVA and ( V_{line} ) is the line voltage in kV.
Given:
– ( S = 10 , text{MVA} )
– ( V_{line} = 11 , text{kV} )
[
I_{line} = frac{10 times 10^6}{sqrt{3} times 11 times 10^3} approx 523.6 , text{A}
]
2. The zero sequence reactance (X0) is given as 10%. We calculate the zero sequence reactance in ohms:
[
X_0 = frac{10}{100} times frac{V_{line}^2}{S}
]
[
X_0 = 0.1 times frac{(11 times 10^3)^2}{10