To calculate the inertia constant ( H ) for the alternator, we can use the formula:
[
H = frac{J cdot omega_s}{S_{base}}
]
Where:
– ( J ) is the moment of inertia in kg·m²
– ( omega_s ) is the synchronous angular speed in rad/s
– ( S_{base} ) is the base apparent power in MVA
Given:
– Moment of inertia, ( J = 27.5 times 10^3 , text{kgm}^2 )
– The rated power of the alternator, ( P = 500 , text{MW} ) which is ( 500 , text{MVA} ) because it’s a three-phase system.
– The synchronous speed ( omega_s ) for a 50 Hz system is given by:
[
omega_s = 2 pi f = 2 pi times 50 approx 314.16 , text{rad/s}
]
Now, substituting the values into the formula:
[
H = frac{27.5 times 10^3 cdot 314.16}{500 times 10^6}
]
Calculating this:
[
H approx frac{27.5 times 10^3 cdot 314.16}{500