To analyze the given problem, we can approach it in a structured manner.
1. Calculate the apparent power (S):
The real power (P) is given as 5 MW and the power factor (pf) is 0.8.
[
S = frac{P}{pf} = frac{5 , text{MW}}{0.8} = 6.25 , text{MVA}
]
2. Calculate current (I):
The voltage at the receiving end (V_R) is 10 kV.
[
I = frac{S}{sqrt{3} cdot V_R} = frac{6.25 times 10^3 , text{VA}}{sqrt{3} cdot 10 times 10^3 , text{V}} = frac{6.25}{sqrt{3} cdot 10} approx 0.361 , text{A}
]
3. Calculate the voltage drop (V_drop) in the line:
Given the resistance (R) is 0.39 Ω and the reactance (X) is 3.96 Ω, we can calculate the voltage drop using:
[
V_{drop} = I cdot Z
]
Where