To find the half voltage regulation, we first need to calculate the voltage regulation and then divide it by 2.
### Step 1: Calculate the receiving end current (I_R)
For an inductive load, the apparent power (S) can be calculated as:
[ S = frac{P}{text{Power Factor}} = frac{5 , text{MW}}{0.8} = 6.25 , text{MVA} ]
The receiving end line current (I_R) can be calculated using:
[ I_R = frac{S}{sqrt{3} cdot V_R} ]
Given ( V_R = 10 , text{kV} = 10,000 , text{V} ):
[ I_R = frac{6,250,000 , text{VA}}{sqrt{3} cdot 10,000 , text{V}} approx frac{6,250,000}{17,320.5} approx 360.6 , text{A} ]
### Step 2: Calculate the voltage drop (V_drop)
Using the transmission line parameters:
– Resistance (R) = 0.39 Ω
– Reactance (X) = 3.96 Ω
– Total impedance (Z) = ( R + jX = 0.39 + j3.96