To find the new power factor at the reduced voltage regulation, we can follow these steps:
1. Determine the current (I) at the receiving end:
[
P = V cdot I cdot text{pf}
]
Rearranging gives:
[
I = frac{P}{V cdot text{pf}} = frac{5,000,000}{10,000 cdot 0.8} = 625 , text{A}
]
2. Calculate the voltage drop (VD) over the transmission line:
[
V_D = I cdot (R + jX) = I cdot R + I cdot jX
]
Where:
– (R = 0.39 , Omega)
– (X = 3.96 , Omega)
[
V_D = 625 cdot (0.39 + j3.96) = 243.75 + j2475 = 243.75 + 2475j , text{V}
]
The magnitude of the voltage drop is:
[
|V_D| = sqrt{243.75^2 + 2475^2} approx 2476.59 , text{V}
]
3