To find the resistance that must be placed in the neutral such that the fault current for a single-phase-to-ground fault does not exceed the rated line current in per unit (pu), we can start by determining the rated current of the alternator.
1. Calculate the rated current (I_rated) of the alternator:
– The base power (S_base) = 10 MVA = 10,000 kVA
– The base voltage (V_base) = 11 kV = 11,000 V
Using the formula:
[
I_{rated} = frac{S_{base}}{sqrt{3} times V_{base}}
]
[
I_{rated} = frac{10,000}{sqrt{3} times 11} approx 523.61 text{ A}
]
2. Determine the sequence reactances in per unit:
– Positive sequence reactance (X_1) = 0.25 pu
– Negative sequence reactance (X_2) = 0.40 pu
– Zero sequence reactance (X_0) = 0.10 pu
3. For a single-phase-to-ground fault:
The fault current (I_f) can be expressed as:
[
I_f = frac{V_{ph}}{Z_{total}}
]