To find the resistance that must be placed in the neutral to ensure that the zero sequence fault current does not exceed the rated line current in per unit (pu), we can follow these steps:
1. Calculate the Rated Line Current:
[ I_{rated} = frac{S_{base}}{sqrt{3} times V_{line}} ]
Where:
– ( S_{base} = 10 , text{MVA} = 10,000 , text{kVA} )
– ( V_{line} = 11 , text{kV} = 11,000 , text{V} )
Computing:
[ I_{rated} = frac{10,000 , text{kVA}}{sqrt{3} times 11 , text{kV}} = frac{10,000}{19.052} approx 524.92 , text{A} ]
Convert this to per unit (pu):
[ I_{rated(pu)} = 1.0 , pu ]
2. Zero Sequence Reactance:
Given ( X_0 = 10% ) of the base, or in per unit:
[ X_0 = 0.1 , pu ]
3. Desired Zero Sequence Fault Current:
The maximum desired zero sequence